Can you describe a little more what you mean by running vent cycles? Are you talking about having vents open periodically, as opposed to constantly?
Also, how would you design the vents inside the room?
Thanks!
A vent cycle means you aren't ventilating the room constantly. So a controller has a deadband setting. You set it to say 80 degrees and a deadband of 5 degrees. The controller will let the temp rise to 80 and kick on the exhaust and/or intake fans to cool the room. Once the room drops to 75 (deadband setting of 5 degrees) the controller turns off the fans. That is a ventilation cycle. This works when the temps rise slowly and you only have to ventilate a few times a day, maybe a couple extra on a really hot day.
A vent cycle could be done for humidity also, if the ambient humidity is lower than your target RH%.
During a vent cycle the controller disables any CO2 enrichment, no reason to blow it all out. Good systems can also be setup to disable a humidification/dehumidification device or heating/cooling device when venting for the other. So say you are venting for high temperature, there is no reason for the dehumidifier to run during the vent cycle.
As to the vents themselves, thats just a blower moving air. It could be a filtered fresh cold air intake. It could be a hot air exhaust. It could be both together. If you want to have no airflow when the blowers are off you can install dampers on the ductwork that will close and open automatically. That prevents high wind from blowing thru your intake. A dust shroom is a good filter for an intake if you can conceal it and protect it from the weather and UV light, I use them in basement window wells and they last a long time, can be washed and reused.
I hope all that helps.